I have done a few accelerators but always as part of a suite and not rated. I may have different suggestions based on who is making the comment (plan checker, inspector, fire marshall, etc.). I will assume the comment is from a plan checker for now.
I personally would respond to the plan checker with something to the effect of:
The purpose of latching is that the door is restrained from opening under the pressure created by a fire. Given the weight of the door and that it is held closed mechanically by a motor, you are complying with the intent of the code. You may have a second problem that has not come up yet. That is the rating of the door & frame. If the manufacture does not have positive latching they may not have a label on the door and frame.
If the simple response to the comment does not work I think I would try to get an "engineering equivalency" or an "alternate means of compliance" if either of these are accepted in Michigan. You will need them for both the door and the latch. I am assuming you can apply a smoke seal if needed.
The arguments for equivalency are:
20 minute door: The concrete (or lead lined) door obviously is capable of withstanding the 20 minutes needed for it's rating.
Positive latching: The purpose of latching is that the door is restrained from opening under the pressure created by a fire. Given the weight of the door and that it is held closed mechanically by a motor, you are complying with the intent of the code.
Engineering judgements or equivalency come from testing companies like UL or Warnock Hersey. Warnock Hersey has relabeled hundreds of doors and/or frames for me over the years. Some of those "relabeling" were for stainless steel frames that were never tested but allowed to be installed in the 50's because they were obviously compliant. That is analogous to your situation so you may want to give them a call.
Good luck!
-------------------------------------------
Mark Paone AIA
Principal
Mark J. Paone, AIA Architect
Orange CA
-------------------------------------------
Original Message:
Sent: 05-16-2014 17:46
From: Heather Lewis
Subject: Latching of Linear Accelerator Doors?
Hello,
It appears that a vendor for Linear Accelerator doors, Veritas, does not have any capacity to latch the door closed. Adding a latch, even would void the warranty. Our regulators, however, point out that a corridor door requires a positive latch. Does anyone else face this issue, and how have you dealt with it?
-------------------------------------------
Heather Lewis AIA
Manager, Architectural Services
University of Michigan Hospitals & Health Services
Ann Arbor MI
-------------------------------------------